Thread: Why is my meter reading 0 voltage across 2 hot legs of a double pole breaker?

  1. #1
    Join Date
    Nov 2009
    Location
    London ON
    Posts
    1,454

    Default Why is my meter reading 0 voltage across 2 hot legs of a double pole breaker?

    I'm installing a new 30 Amp 220V 1ph circuit for a table saw. I have a double pole breaker with 2 hots and a ground. The ground wire is continuous to the saw and grounded in the box.

    My meter reads 110v hot to ground on both legs but 0 across the 2 hots and my saw won't start. I have power going to the magnetic starter but she won't fire up.

    In the panel on the other side I have 3 220v circuits wired exactly the same and I get 220 across the hot legs on all three breakers and machines run fine on them.

    I swapped out the offending breaker for a brand new one, same deal. I put a second double pole breaker on the same side of the panel I'm wiring and I get 110v hot to ground but again I get 0v across the hots.

    I get 220 across the hots at the bus bar.

    Can anyone tell me what is going on?

  2. #2
    Join Date
    Jul 2008
    Location
    Penetanguishene, ON
    Posts
    3,164
    Blog Entries
    1
    Real Name
    Ummmm....Frank? :-)

    Default Re: Why is my meter reading 0 voltage across 2 hot legs of a double pole breaker?

    I'll betcha you have a Federal panel......am I right?

    If I am, You have both terminals sharing the same leg, so you'll have to move the breaker up or down one slot.
    I dream of a better world, one where chickens can cross roads without having their motives questioned.

  3. #3
    Join Date
    Nov 2009
    Location
    London ON
    Posts
    1,454

    Default Re: Why is my meter reading 0 voltage across 2 hot legs of a double pole breaker?

    Quote Originally Posted by Ryan Shervill View Post
    I'll betcha you have a Federal panel......am I right?

    If I am, You have both terminals sharing the same leg, so you'll have to move the breaker up or down one slot.
    Yessiree I do. I'm going to try that right now. Thanks!

  4. #4
    Join Date
    Jul 2008
    Location
    Penetanguishene, ON
    Posts
    3,164
    Blog Entries
    1
    Real Name
    Ummmm....Frank? :-)

    Default Re: Why is my meter reading 0 voltage across 2 hot legs of a double pole breaker?

    Quote Originally Posted by dave_k View Post
    Yessiree I do. I'm going to try that right now. Thanks!
    Believe me, you are not the first to run into this with Federal panels.....they are nice, but man can they be counter-intuitive to put breakers into.
    I dream of a better world, one where chickens can cross roads without having their motives questioned.

  5. #5
    Join Date
    Nov 2009
    Location
    London ON
    Posts
    1,454

    Default Re: Why is my meter reading 0 voltage across 2 hot legs of a double pole breaker?

    I just moved everything down a slot and it works fine. Thanks again Ryan

  6. #6
    Join Date
    Jul 2008
    Location
    Penetanguishene, ON
    Posts
    3,164
    Blog Entries
    1
    Real Name
    Ummmm....Frank? :-)

    Default Re: Why is my meter reading 0 voltage across 2 hot legs of a double pole breaker?

    Awesome Glad it was an easy fix.

    Ryan
    I dream of a better world, one where chickens can cross roads without having their motives questioned.

Similar Threads

  1. Note! This Is Required Reading For All Men!
    By StephenL in forum Off Topic
    Replies: 4
    Last Post: 02-15-2010, 09:16 PM
  2. Some interesting reading
    By Pete in Welland in forum Turning
    Replies: 8
    Last Post: 10-14-2008, 05:37 AM
  3. What are you reading?
    By J.P. Rap in forum Off Topic
    Replies: 22
    Last Post: 05-23-2008, 11:51 PM
  4. Kindergarten reading bench
    By Woodwreck in forum Woodworking
    Replies: 0
    Last Post: 01-28-2008, 10:05 PM
  5. Reading material
    By danpower in forum Woodworking
    Replies: 4
    Last Post: 12-05-2006, 12:33 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •